4-20mA Vs Voltage Signals??

Posted: 26 Apr 2010, 12:49
by sameenkhan
Hi Guys,

In most industries, Why 4-20mA signal is more preferred over voltage signals, WHY??

Regards,
Sameen

Re: 4-20mA Vs Voltage Signals??

Posted: 02 Jun 2010, 13:35
by ali.abbas
because in series loops current would remain unchanged whereas voltage would drop due to resistance esp. if the signal cable used has high resistance. Using voltage levels would mean the measurement would not be a perfect indication of the actual process parameter being monitored ...

Re: 4-20mA Vs Voltage Signals??

Posted: 30 Aug 2010, 03:53
by ali.abbas
Sameen,

Go thru this. Its a more detailed answer to your initial query, and basically just builds on to my previous reply. I came across this while surfing the net, thought you might be interested too.
A current source generates as much or as little voltage as needed across its leads to produce a constant amount of current through it. This is just the opposite of a voltage source (an ideal battery), which will output as much or as little current as demanded by the external circuit in maintaining its output voltage constant. Following the "conventional flow" symbology typical of electronic devices, the arrow points against the direction of electron motion. Apologies for this confusing notation: another legacy of Benjamin Franklin's false assumption of electron flow!

Image

Current sources can be built as variable devices, just like voltage sources, and they can be designed to produce very precise amounts of current. If a transmitter device were to be constructed with a variable current source instead of a variable voltage source, we could design an instrumentation signal system based on current instead of voltage:

Image

The internal workings of the transmitter's current source need not be a concern at this point, only the fact that its output varies in response to changes in the float position, just like the potentiometer setup in the voltage signal system varied voltage output according to float position.

Notice now how the indicator is an ammeter rather than a voltmeter (the scale calibrated in inches, feet, or meters of water in the tank, as always). Because the circuit is a series configuration (accounting for the cable resistances), current will be precisely equal through all components. With or without cable resistance, the current at the indicator is exactly the same as the current at the transmitter, and therefore there is no error incurred as there might be with a voltage signal system. This assurance of zero signal degradation is a decided advantage of current signal systems over voltage signal systems.

The most common current signal standard in modern use is the 4 to 20 milliamp (4-20 mA) loop, with 4 milliamps representing 0 percent of measurement, 20 milliamps representing 100 percent, 12 milliamps representing 50 percent, and so on. A convenient feature of the 4-20 mA standard is its ease of signal conversion to 1-5 volt indicating instruments. A simple 250 ohm precision resistor connected in series with the circuit will produce 1 volt of drop at 4 milliamps, 5 volts of drop at 20 milliamps, etc:


----------------------------------------
| Percent of | 4-20 mA | 1-5 V |
| measurement | signal | signal |
----------------------------------------
| 0 | 4.0 mA | 1.0 V |
----------------------------------------
| 10 | 5.6 mA | 1.4 V |
----------------------------------------
| 20 | 7.2 mA | 1.8 V |
----------------------------------------
| 25 | 8.0 mA | 2.0 V |
----------------------------------------
| 30 | 8.8 mA | 2.2 V |
----------------------------------------
| 40 | 10.4 mA | 2.6 V |
----------------------------------------
| 50 | 12.0 mA | 3.0 V |
----------------------------------------
| 60 | 13.6 mA | 3.4 V |
----------------------------------------
| 70 | 15.2 mA | 3.8 V |
----------------------------------------
| 75 | 16.0 mA | 4.0 V |
---------------------------------------
| 80 | 16.8 mA | 4.2 V |
----------------------------------------
| 90 | 18.4 mA | 4.6 V |
----------------------------------------
| 100 | 20.0 mA | 5.0 V |
----------------------------------------


The current loop scale of 4-20 milliamps has not always been the standard for current instruments: for a while there was also a 10-50 milliamp standard, but that standard has since been obsoleted. One reason for the eventual supremacy of the 4-20 milliamp loop was safety: with lower circuit voltages and lower current levels than in 10-50 mA system designs, there was less chance for personal shock injury and/or the generation of sparks capable of igniting flammable atmospheres in certain industrial environments.

Re: 4-20mA Vs Voltage Signals??

Posted: 30 Aug 2010, 07:01
by katieburton12
If I am right, CB-50 without a terminal component as resistance. analog input of the government has a high impedance much greater than the resistance you need a direct current voltage. Since the value of the proposed Kid 250E is normal. Mostly the area is 50-250 ohms. Energy source to drive at this time, regardless of the value of resistance. Within and between, of course.