Attachment to tanks after hydrostatic testing
Posted: 08 Oct 2010, 18:44
by octane
We have conducted hydrostatic testing at our tank and now for insulation / cladding sheets hook up, we need to attach small attachments with welding.
Is that allowable as per code? Or do we need to conduct hydrostatic testing again?

Re: Attachment to tanks after hydrostatic testing
Posted: 09 Oct 2010, 11:28
by arcpro
As per API 650 you can weld the non-structural attachments to the tank even after hydrostatic testing.
Your case also appears to be the same. No re-hydro required.
Re: Attachment to tanks after hydrostatic testing
Posted: 09 Oct 2010, 17:10
by octane
Thanks.
In which clause this has been mentioned?
Re: Attachment to tanks after hydrostatic testing
Posted: 11 Oct 2010, 06:37
by arcpro
Look in sec. 5.3.5 API 650 (2003 edition)
Re: Attachment to tanks after hydrostatic testing
Posted: 11 Oct 2010, 15:12
by octane
Thanks...
I found that.