Understanding use of Limit Switches
Posted: 08 Oct 2010, 03:59
Quoted information has been extracted from another website. It gives an amazing overview of the use of limit switches with control valves in particular.
Source: http://www.driedger.ca/limitsw/LimitSw.html
Source: http://www.driedger.ca/limitsw/LimitSw.html
continued on next post....INTRODUCTION:
There is a great variety of possible combinations for installing and connecting limit switches on valves. The number of switches depends on the particular control objective and may be influenced by redundancy considerations. The way they are connected depends on the safety and reliability requirements. In order to clarify this discussion, diagrams like Figure 1 will be used. All signals, switch positions, etc. are shown with the valve at the center of travel. No limit switches are actuated, all are shown in their shelf position as determined by their internal springs. Imagine the valve to be like a guillotine where the stem travels upward to open the valve and downwards to close it. The diagrams show the switches connected to indicating light bulbs but the logic is identical if a DCS or other form of MMI is used.
The limit switch that is actuated when the valve is fully open is labeled ZSO. The one at the extreme opposite end is labeled ZSC.
The terminals on the electrical switches are labeled Common (C), Normally Open (NO), and Normally Closed (NC). This unfortunate choice of terminology has nothing to do with the state of the valve nor even the "normal" position of the switch. It refers to the state of the switch when nothing is pushing on it.
SINGLE SWITCH, DIRECT APPROACH: A single limit switch at the OPEN end of the valve (ZSO), as shown in Figure 2, will tell us when the valve is fully open. It cannot tell us if the valve is fully closed. The problem is that the term "open" is a bit ambiguous. Question: Is a half-open valve open, closed, neither open nor closed, or both open and closed? This discussion will use the following definitions:According to these definitions the half-open valve is both open and closed. A single ZSO switch can only tell us if the valve is "fully open" and "not closed". It cannot tell us if the valve is partly open.
- OPEN = Partly or fully OPEN
CLOSED = Partly or fully CLOSED
Not OPEN = Fully CLOSED
Not CLOSED = Fully OPEN
Example 1: We need a limit switch and a status light to tell the operator that the fuel gas to a furnace is OPEN. If so, it is not safe to begin the light-off sequence. A ZSC switch at the closed end of travel is used so that we can be sure the valve is "fully closed" and "not open" even a little bit. The correct contact is NC. If the valve is even the slightest bit open, the OPEN light comes on.
Example 2: We need a limit switch and a status light to tell the operator that the fuel gas to a furnace is CLOSED. If so, it is safe to begin the light-off sequence. This is exactly the same limit switch as before: ZSC. We want to know if the valve is "fully closed". The only difference is that Example 1 uses the NC contact of the switch to turn off an OPEN light when the valve is not fully open while Example 2 uses the NO contact to turn on a CLOSED light when the valve is fully closed.
SINGLE SWITCH, FAILSAFE:
"Failsafe" is a much abused word. It is very dramatic because it combines the apparently contradictory concepts of failure and safety in a single word. The reality is not so dramatic. It means that the failure of a component is unlikely to cause any harm. The formal definition I prefer is:
A FAILSAFE design is one in which the most probable failure mode results in the most probably safe condition.
Note that there are several "probablies" in this definition. Failsafe design is a technique for stacking the deck in favor of safety. It does not guarantee safety but it makes it more probable. The Examples 1 and 2, above, accomplish exactly the same thing. The difference is in the behaviour of the two methods when failures occur. Table 1 shows all the possible modes of failure. All those failure modes marked "*" result in the bulb failing to light. The most probable failures are marked "+". For an arrangement like that of Example 1, there are eleven failures that would lead the operator to believe that the valve is not OPEN and to proceed to light the furnace. An explosion could result. Of these 11 possible failures, 6 have high probability. This would not be a failsafe arrangement!
If the circuit is arranged as in Example 2 and any of the above mentioned eleven failures occurred, the operator would conclude that the valve is not CLOSED and would attempt to close the valve. The CLOSED light would still not come on. He would then, we hope, call maintenance to find the cause of the problem. Of the two possible circuits, Example 2 is the one that is most probably safe.
In the case of Example 2, only failures 5, 7, and 10 could give the operator unsafe information. Note that these three are all low probability failures.
Thus we have eleven safe failures and three unsafe failures. All the most probable failures result in the same safe response: The operator does not attempt to light the furnace. Example 2 is a failsafe arrangement. The odds in favor of safety are greatly improved.
- 5. Limit switch fails to return
7. Limit switch fails as short circuit
10. Signal wire shorts to power