in my case how we can inspect the buried pipeline of cooling water system
there is no CP system installed
and diameter of line varies i.e min 2inch and max 8inch
kindly tell me other than LRUT?
if possible then tell me conventional technique
Inspection of Cooling Water System
Inspection of Cooling Water System
Sakib Jalal
-
qaisarabbas
- Core Member
- Posts: 134
- Joined: 23 Mar 2010, 15:21
- Area of interest: Metallurgy Engineering
Re: Inspection of Cooling Water System
For external corrosion, carry out DCVG or CIPS and find out the defective coating - a prime source of external pitting / crevice corrosion. For internal corrosion, carry out LRUT or Pulse-Echo UT at random locations for internal thinning. Inspection of all pipe risers is must for soil-to-air interface corrosion.
Q. Abbas
-
Nabeel Ahmed Qureshi
- Core Member
- Posts: 87
- Joined: 04 Apr 2010, 09:38
- Area of interest: Mechanical Engineering
Re: Inspection of Cooling Water System
If this is about plant piping then you need to perform Bell hole inspections i.e excavate & expose the line at different locations & do visual inspections to check the wrapping condition.You can check the thickness thru manual UT.DCVG/C-scan/CIPS is only give results on cross country pipings.
Hope this would help.
NAQ
Hope this would help.
NAQ
-
Nabeel Ahmed Qureshi
- Core Member
- Posts: 87
- Joined: 04 Apr 2010, 09:38
- Area of interest: Mechanical Engineering
Re: Inspection of Cooling Water System
Sakib,
Underground piping without CP system is a crime. You should propose your management to install CP system so that your piping has adequate protection available against corrosion.
Regards
NAQ
Underground piping without CP system is a crime. You should propose your management to install CP system so that your piping has adequate protection available against corrosion.
Regards
NAQ
Re: Inspection of Cooling Water System
@ QAISER
is DCVG is not applicable only when u have CP system installed???
@nabeel
for bell hole inspection
will you elaborate that what are the points that need to excavate other than branch connection and risers?
ya piping without cp is crime and i propose this to mangment nowdays i am working on it
is DCVG is not applicable only when u have CP system installed???
@nabeel
for bell hole inspection
will you elaborate that what are the points that need to excavate other than branch connection and risers?
ya piping without cp is crime and i propose this to mangment nowdays i am working on it
Sakib Jalal
Re: Inspection of Cooling Water System
i have read the manual provided by one of this forum
in it i have come to know about the inspection of piping system IN IT i read that wrapping and coating of underground pipings having no CP system can be ensured by using pearson survey meter
my question is that is it possible via it and if yes then what the procedure for it ?????????
as i used this technique on piping system having CP system installed
in it i have come to know about the inspection of piping system IN IT i read that wrapping and coating of underground pipings having no CP system can be ensured by using pearson survey meter
my question is that is it possible via it and if yes then what the procedure for it ?????????
as i used this technique on piping system having CP system installed
Sakib Jalal