Incident during piping clamp sealing works

Post by sys1 »

Recently came to know about an incident which happened in Liaoning Province Panjin Haoye Chemical when there was piping clamp sealing activities were undergoing.
During this activity, piping horizontal portion weld got ruptured leading to a leak catching an ignition source (non-explosion proof walkie-talkies) result in fire.
We as Operations issue to our maintenance personnel work permits to perform sealing & re-sealing of such piping clamps installed on either on weak line or having an active leak.
How strongly we need to check for the controls to avoid such an incident (leak during sealing)?
octane
Posts: 204
Joined: 08 Oct 2010, 15:38
Area of interest: Mechanical Engineering

Re: Incident during piping clamp sealing works

Post by octane »

Thank you for sharing this.
I would say there are many lessons to be learnt from this incident. Though I would like to know more details which unfortunately I was unable to obtain however, primary concern here is the inspection of further deterioration once a temporary solution is applied. The service was flammable and an injection sealing was applied. The actual pipe wall might have been got thinned enough to witness a rupture of weld joint. That is required to be monitored by Inspection authorities before allowing maintenance performing injection job. A type of temporary repair which masks further inspection of pipe wall could result into an asset related incident. There must have been some active internal damage mechanism causing this to happen.
neo
Posts: 139
Joined: 12 Jul 2025, 09:25
Area of interest: Chemical Engineering

Re: Incident during piping clamp sealing works

Post by neo »

From operations & maintenance point of view, it is important that Contractor must produce a method statement which should be verified by technical body for re-injection of sealant. Considering flammable service, job should be regarded as critical as there could be a leak during this work.
I am thinking about knowing the piping condition better before doing re-injection. Use of sealant means presence of an active leak and injection pressure has to be 1.1 - 1.3 times greater the operating pressure. Pipe wall would handle that externally or not might have been the issue here.
irish
Posts: 148
Joined: 27 Nov 2010, 09:04
Area of interest: Mechanical Engineering

Re: Incident during piping clamp sealing works

Post by irish »

It has been very clearly mentioned that the initial root cause include using of carbon steel component instead of stainless steel one as recommended before.
Internal corrosion case and then that was externally clamped with flammable compound inside. Clamp after all needs to be mounted on the healthy portion of the piping.
A timely action to resolve the issue was needed instead of just sealing as and when required.