Temporary Repair Failure

Materials Science, Metallurgy, Welding, NDTs, Reliability Assessment, Failure Analysis, etc.
Post Reply
ben
Posts: 250
Joined: 24 Aug 2010, 03:11
Area of interest: Mechanical Engineering

Temporary Repair Failure

Post by ben »

Copying from an incident reported in 2012;

What Happened:
Ice formation was reported on the 3rd stage relief line on the associated gas compressor. A
pinhole leak was found and a wrap temporary repair was effected, following Technical
Authroity approval. The wrap was applied by a specialist vendor.
Approximately 9 days later a smell of gas (confirmed using ‘snoop’) was picked up at the wrap
repair. Bubbling & discolouration of the wrap was also noticed suggesting the wrap had
failed.

Lesson Learnt:
The cause of the wrap failure was initially thought to be insufficient curing time of the resin,
however following further analysis it was established that the surface temperature of the
pipework during application of the wrap was too low leading to a lack of adhesion between the
wrap material/resin and the pipework. It was also considered that inadequate pressure being
applied during the wrap application contributed to the premature failure of the repair which
was identified as a contributory factor.
The lesson learnt is to always ensure the pipe having the wrap applied is brought up to the
correct temperature, as per manufacturers guidance prior to application of the wrap.

Attached is the full form for reference.
For sharing & discussion purposes.
349860088-Incident-Alert-Wrap-Failure.pdf
You do not have the required permissions to view the files attached to this post.
neo
Posts: 98
Joined: 12 Jul 2025, 09:25
Area of interest: Chemical Engineering

Re: Temporary Repair Failure

Post by neo »

There are instance where temporary repairs have failed and the major reason include:
1. Engineering standards non-compliance
2. Lapse inspection /maintenance
3. Installation practices
I recall a case where a box-up repair was carried out by an external contractor which upon no proper sealing injection started leaking within 2 years time.

Thanks for sharing this.
irish
Posts: 114
Joined: 27 Nov 2010, 09:04
Area of interest: Mechanical Engineering

Re: Temporary Repair Failure

Post by irish »

BP Grangemouth Refinery reported a failure from a temporary repair actually happened due to lack of attention towards converting a temporary repair to a permanent solution.
octane
Posts: 166
Joined: 08 Oct 2010, 15:38
Area of interest: Mechanical Engineering

Re: Temporary Repair Failure

Post by octane »

Temporary repairs are required to be managed very well.
Internal thinning, damage mechanism is active all throughout and with no finite time of converting that to a permanent one would actual pose a risk.
Corrosion rates, associated piping inspection, localized monitoring, there are quite a lot of factors affecting the useful life of any temporary repair.
irish
Posts: 114
Joined: 27 Nov 2010, 09:04
Area of interest: Mechanical Engineering

Re: Temporary Repair Failure

Post by irish »

Dependency on external support to engineer & manage the temporary repairs is required to be reinforced with engineering review & procedural /auditable management performed by on-site team.
Over and above this, a periodic review, inspection is needed which is to be defined, and reported. Based upon this, changes could be required to be made to existing repairs.
novice123
Posts: 133
Joined: 24 Jul 2010, 18:32
Area of interest: Petroleum Engineering

Re: Temporary Repair Failure

Post by novice123 »

Thanks for sharing.
ben
Posts: 250
Joined: 24 Aug 2010, 03:11
Area of interest: Mechanical Engineering

Re: Temporary Repair Failure

Post by ben »

The thing is that we still applyvwraps every now and then when needed, that too on hydrocarbon lines. Temperature of the line contributes a lot to the installation of the wrap and then the applied pressure during installation.
I understand that any wrapping done to arrest a leak temporarily must be applied with a method statement in place and not only that, ther should be a documented and signed inspection plan to follow all the critical activities during the installation.
Post Reply