Overdue maintenance of shutdown systems

Post by opo21 »

What actually sites do when there is an overdue maintenance for shutdown systems?
Performing risk assessment? What actually is discussed to assess the risk?
Please share how this all goes when happens.
tuan
Posts: 103
Joined: 27 May 2025, 14:07
Area of interest: Chemical Engineering

Re: Overdue maintenance of shutdown systems

Post by tuan »

Is this function credited in the hazard analysis as a risk-reduction barrier?
If yes, this has to be a process safety issue and require a formal team risk assessment requiring approval from technical authorities.
The degradation is required to be captured as focused barrier one.
Complete enlisting of remaining independent protection systems is needed:
Relief valves
Operator response
Alarms
Mechanical design margin
Other SIS layers
Passive safeguards
opo21
Posts: 35
Joined: 22 Dec 2025, 08:14
Area of interest: Chemical Engineering

Re: Overdue maintenance of shutdown systems

Post by opo21 »

Risk assessment is what we have been doing to register this as a process safety deviation.
And all the barriers which should be supporting are being considered as their availability matters during this time.
But the issue is that this still happens, and requires to be lived with.
Are there ways to avoid overdue maintenance of such shutdown systems?
What about looking into the past data, current maintenance history or any other test which could provide the assurance rather declaring all this, and performing formal risk assessments?
tuan
Posts: 103
Joined: 27 May 2025, 14:07
Area of interest: Chemical Engineering

Re: Overdue maintenance of shutdown systems

Post by tuan »

See just have a look into the current frequency of the pM plans in place.
To perform shutdown based PMs, they should be aligned with the shutdown plan otherwise, you will end up saying the same things, PM overdue.
And if not possible to align, then yes, risk assessment for every overdue PM is a must to do thing.
You won't be able to do anything about the consequence while estimating the risk but the probability part can be properly calculated based upon historical data.
ivani1
Posts: 93
Joined: 25 May 2025, 14:25
Area of interest: Mechanical Engineering

Re: Overdue maintenance of shutdown systems

Post by ivani1 »

This is important.
While you perform the risk assessment, now the shutdown system cannot be assured of its performance, all these listed systems by tuan are required to be considered as available mitigations. I am not sure how are you making sure about the assurance of mitigations health?
tuan wrote: 20 Jan 2026, 18:09 Is this function credited in the hazard analysis as a risk-reduction barrier?
If yes, this has to be a process safety issue and require a formal team risk assessment requiring approval from technical authorities.
The degradation is required to be captured as focused barrier one.
Complete enlisting of remaining independent protection systems is needed:
Relief valves
Operator response
Alarms
Mechanical design margin
Other SIS layers
Passive safeguards
opo21
Posts: 35
Joined: 22 Dec 2025, 08:14
Area of interest: Chemical Engineering

Re: Overdue maintenance of shutdown systems

Post by opo21 »

That is another point ivani1. We set something to act as a mitigation, and then we forget the health of such mitigations in place.
I would call for an intelligent system locking these mitigations once assigned to a downgraded situation or to a process safety risk.
ivani1 wrote: 07 Feb 2026, 07:04 This is important.
While you perform the risk assessment, now the shutdown system cannot be assured of its performance, all these listed systems by tuan are required to be considered as available mitigations. I am not sure how are you making sure about the assurance of mitigations health?
tuan wrote: 20 Jan 2026, 18:09 Is this function credited in the hazard analysis as a risk-reduction barrier?
If yes, this has to be a process safety issue and require a formal team risk assessment requiring approval from technical authorities.
The degradation is required to be captured as focused barrier one.
Complete enlisting of remaining independent protection systems is needed:
Relief valves
Operator response
Alarms
Mechanical design margin
Other SIS layers
Passive safeguards