Hi Guys,
For a SIS, what typical Proof Test interval is set at your plant??
Regards,
Sameen
Proof Test Interval at you Plant??
-
sameenkhan
- Posts: 32
- Joined: 07 Apr 2010, 17:54
- Area of interest: Electrical Engineering
- Contact:
-
ali.abbas
- Core Member
- Posts: 61
- Joined: 25 May 2010, 23:26
- Area of interest: Inst. & Control Engineering
Re: Proof Test Interval at you Plant??
Sameen,
At our plant, the current practice is to check the primary sensing element on an annual basis.
Complete logic verification is carried out once in 1 or 2 years or during plant outage depending on
1- criticality of service
2- whether the activity can be carried online or not.
Hope your questions answered.
Regards,
Ali Abbas